Good troubleshooting so far. Now that you know a ground signal will start the intended zones. And you know the purpose of the relay is to convert the 12V pos signal from the tstat into a ground signal that the AH is looking for.
Confirm you are getting a a 12V signal from the tstat at the relay terminal.
Confirm the relay is wired correctly, when it is triggered the contacts should make to ground.
Good troubleshooting so far. Now that you know a ground signal will start the intended zones. And you know the purpose of the relay is to convert the 12V pos signal from the tstat into a ground signal that the AH is looking for.
Confirm you are getting a a 12V signal from the tstat at the relay terminal.
Confirm the relay is wired correctly, when it is triggered the contacts should make to ground.