No fan or heat from zones A or C
#5

Tyler,

Good troubleshooting so far. Now that you know a ground signal will start the intended zones. And you know the purpose of the relay is to convert the 12V pos signal from the tstat into a ground signal that the AH is looking for.

Confirm you are getting a a 12V signal from the tstat at the relay terminal.
Confirm the relay is wired correctly, when it is triggered the contacts should make to ground.