03-11-2021, 04:47 PM
I need to under-extend the slide (thanks Tom for the article links) to do some work around the seal. The slide room worked perfectly this morning in both directions. I extended the slide room fully and then retracted it about 1/2 way so I could get to the limit switch to make the slide room under-extend. I removed the limit switch and attempted to retract the room. Nothing, nada... I can hear the pump running so I checked the fuses 85,86,87,90 as suggested in the Rosetta Stone of HWH diagrams. The fuses were good (tested with an ohm meter). I checked at the solenoids to make sure I was getting 12-volts to them - the unlock wire is energized when the retract or extend button is pushed (and the locks themselves are open/retracted). The extend and retract wires are not getting anything...
So I decided to jump the unlock wire to the retract solenoid just to check it but still nothing - a test light confirmed that there was 12-volts through the wire to the solenoid...
Any ideas?
BTW, does anyone have the diagram showing which solenoid does what? I can’t find it in the search... I think mine may be backwards now :-(
Thanks! Adrian
So I decided to jump the unlock wire to the retract solenoid just to check it but still nothing - a test light confirmed that there was 12-volts through the wire to the solenoid...
Any ideas?
BTW, does anyone have the diagram showing which solenoid does what? I can’t find it in the search... I think mine may be backwards now :-(
Thanks! Adrian